Posted By: jimbob old knob and toob wire - 12/15/09 01:14 AM
in nova scotia it used to be code that if you couldnt remove all the old knob and toob when doing a rewire you could put that circuit on a gfci, usually by panel.could some tell me if this is still code.
Posted By: HotLine1 Re: old knob and toob wire - 12/15/09 02:03 AM
Jimbob:
Welcome to the ECN forums! One of my neighbors up north of the border will jump in & give you an answer!

Posted By: dougwells Re: old knob and toob wire - 12/15/09 04:40 AM
Originally Posted by jimbob
in nova scotia it used to be code that if you couldnt remove all the old knob and toob when doing a rewire you could put that circuit on a gfci, usually by panel.could some tell me if this is still code.

yes it is still code
Posted By: jimbob Re: old knob and toob wire - 12/15/09 12:17 PM
its nice to remove all the old wiring but you sometimes cant get it all. thanks for info.
Posted By: mikesh Re: old knob and toob wire - 12/15/09 11:15 PM
One word of caution about rewire and Knob and Tube. Yes it is Kosher and compliant to gfci protect the first outlet and put regular 3 wire receptacles on the circuit. I like to see the outlets downstream with lables indicating they are GFCI protected and don't have a bonding conductor.
The big problem with K&T is the temperature rating and newer luminaires. Many newer luminaires are to be connected to a wire with a 90 degree temperature rating. Trouble is K&T is only 60 degree insulation so a new fixture could destroy the insulation in short order.
New fixture also rewuire a bonding connection and some jurisdictions will allow the circuit to be gfci protected without adding the bonding wire. Check with your inspector.
Posted By: sparky Re: old knob and toob wire - 12/16/09 12:53 AM
so would adding a few inches of newer 90C wire in the box bettween the K&T and fixture wire(s) make this compliant mikesh?

~S~
Posted By: frenchelectrican Re: old knob and toob wire - 12/16/09 03:26 AM
Originally Posted by sparky
so would adding a few inches of newer 90C wire in the box bettween the K&T and fixture wire(s) make this compliant mikesh?

~S~


For my answer is no it is not compliant at all due the oringal T&K do not have grounding conductor there at all and I did recall the NEC stated that you can not extend the groundless conductors.

Merci,Marc
Posted By: mikesh Re: old knob and toob wire - 12/22/09 12:00 AM
For circuits originally supplied with a bonding wire IE nmd3 or MD about 450 mm of 90 loomex will look after the heat issue but the bonding cannot be done from a K&T circuit.
I don't mean 18 inches of wire in the box either. You need to add a jb. If you have attic space it is easy to relocate the old Jb in the rafter and put a new one with the higher temp wire in the place of the ceiling outlet.
Posted By: sparky Re: old knob and toob wire - 12/23/09 01:57 PM
intersting, so would said JB be plastic, and the bonding wire taken out of the 90 loomex here (assuming a K&T circuit without one) ?

~S~
Posted By: Sixer Re: old knob and toob wire - 12/29/09 07:58 AM
Originally Posted by mikesh
If you have attic space it is easy to relocate the old Jb in the rafter and put a new one with the higher temp wire in the place of the ceiling outlet.


If you have attic space then there should be no reason why the knob and tube can't be replaced.

Knob and tube wiring is 60+ years old, has no ground, and SHOULD be replaced, regardless of the condition. Everything has a lifespan, including wiring.

Just because the Code allows us to protect a K&T circuit with a ground fault protector or install a loomex jumper (or high temp sleeving) to make fixture boxes 90C compliant, in my opinion it should only be used as a temporary measure until replacement is done. I'll get down off my soapbox now smile
Posted By: sparky Re: old knob and toob wire - 12/29/09 12:09 PM
so is there a defined life span of wiring methods?

where would one reference this?

~S~
Posted By: mikesh Re: old knob and toob wire - 01/04/10 07:01 PM
Sparky

There is always a design limit but it is not necessarily defined. It is the point where all the materials science runs out of data. For example a spec for sunlight resistance might require some type of insulation to withstand exposure to sunlight for 20 years. Well they don't stick the wire outside and wait 20 years. They stick the wire in a box and shine artificial light on the insulation for a period of time and at an intensity high enough to simulate 20 years of exposure. In the real world some will be installed in Arizona and some in Alaska. The UV protection is the same but the wire in Arizona is more likely to fail sooner than the wire in Alaska. The wire was engineered to last a period of time and any day after that is bonus.

So how long is a lifetime? I have heard that electrical equipment is engineered for something like 40 years. So we don't replace it at 41 years but the design was for 40 years and every day beyond is bonus. Our older houses were designed to accommodate a light bulb and a plug in every room. Most outlets beyond those installed for appliances were also expected to accommodate a plug in light since not that many other household appliances existed. We overloaded these circuits and overheated the wires. The insulation degrades and gets brittle from heat. Eventually the wire will lose it's protection and become a hazard.
There has also been the handyman adding and modifying the circuit as well as new hotter fixtures being connected.
The wiring system is on borrowed time. Even the newest K & T is at least 50 to 60 years old. It is all borrowed time. Sure there are houses where the old wiring is in pristine condition and serving the same function but there is no data to indicate the date of ultimate failure. Maybe it is 500 years or 200 but we all see that these old systems are on average, past the expiry date. Old wiring might last a very long time and well past the original design but like everything, it all eventually fails.
If only a product could predict its last day of operation and account for all the variables of use and abuse. We would wake up one morning and the circuit for the counter would just dissolve or stop working without all the safety hazards. The house computer could have called the electrician and arranged replacement dates and scheduled a work plan. It could predict what parts of the system are soon to fail and we would always have an up to date and failsafe system.
Posted By: sparky Re: old knob and toob wire - 01/05/10 01:26 AM
Originally Posted by mikesh
Sparky

There is always a design limit but it is not necessarily defined. It is the point where all the materials science runs out of data. For example a spec for sunlight resistance might require some type of insulation to withstand exposure to sunlight for 20 years. Well they don't stick the wire outside and wait 20 years. They stick the wire in a box and shine artificial light on the insulation for a period of time and at an intensity high enough to simulate 20 years of exposure. In the real world some will be installed in Arizona and some in Alaska. The UV protection is the same but the wire in Arizona is more likely to fail sooner than the wire in Alaska. The wire was engineered to last a period of time and any day after that is bonus.


interesting, i read something similar in one of the trade mags about how they tested circuit breakers, solo, by itself. My first thought was all the 'real world' applications, like being sanwhiched bettween other breakers (amibent heat)

Quote
So how long is a lifetime? I have heard that electrical equipment is engineered for something like 40 years. So we don't replace it at 41 years but the design was for 40 years and every day beyond is bonus. Our older houses were designed to accommodate a light bulb and a plug in every room. Most outlets beyond those installed for appliances were also expected to accommodate a plug in light since not that many other household appliances existed. We overloaded these circuits and overheated the wires. The insulation degrades and gets brittle from heat. Eventually the wire will lose it's protection and become a hazard.


No argument here, i've filled more dumpsters with K&T and/or BX than i care to recall, many many 'brittle' terminations, etc....


Quote
There has also been the handyman adding and modifying the circuit as well as new hotter fixtures being connected.


the bane of our profession....

Quote
The wiring system is on borrowed time. Even the newest K & T is at least 50 to 60 years old. It is all borrowed time. Sure there are houses where the old wiring is in pristine condition and serving the same function but there is no data to indicate the date of ultimate failure. Maybe it is 500 years or 200 but we all see that these old systems are on average, past the expiry date. Old wiring might last a very long time and well past the original design but like everything, it all eventually fails.


The problem is two fold then, we are not talking milk here, there's no expiration date , and in truth the manufacturers aren't about to make anything that is 'large print'.

Who can blame them really?

next is the 'if it ain't broke, don't fix it' contingent, and i'm sure nobody here needs a lecture on those sorts....

Quote
If only a product could predict its last day of operation and account for all the variables of use and abuse. We would wake up one morning and the circuit for the counter would just dissolve or stop working without all the safety hazards. The house computer could have called the electrician and arranged replacement dates and scheduled a work plan. It could predict what parts of the system are soon to fail and we would always have an up to date and failsafe system.


true that we could have some better , or maybe more inclusive assessment system , weather it be outside intervention (annual inspections like fire alarms?) , or internal assessors (like enhanced software)

this , however, is where credit might (just might) be given to where it's due.

Because now we have the mighty afci, which i'm to understand mitigates both series as well as parralel faults. So it would seem reasonable to consider them, given series being the major brittle factor fault in K&T

This , of course, would be in lieu of a rewire job, but if we are going to buy time until then, i would , and have , suggested it a viable 'bandiad'

In fact, i've garnered one insurance company that's signed onto this idea, and kept a K&T infested coffee shop in town under their coverage for the time being

Further still, one could , at the panel, place a gfci after the afci, couldn't they? The next step is chasing down the brittlisms that cause it all to trip.

Yes , i know, 'bandaids' stick around long enough to be voting age, a problem in of itself. But faced with say, a 10K rewire , as well as the cost of imported french wallpaper being replaced, why can't this be a consideration?

~S~

Posted By: jimbob Re: old knob and toob wire - 01/05/10 03:46 AM
i agree but some people are not willing to rip up floors and ceilings.i thought if it was still flexable without breaking the insulation it was still good.not the best by any means. thanks for all the insight.
Posted By: mikesh Re: old knob and toob wire - 01/05/10 08:05 PM
I can appreciate that selling a rewire in an old house has its challenges. I'd caution That assuming the wire is in good shape because it is flexible where you can get to it and thinking it is in the same shape where it is concealed is a dangerous assumption.
It is just impossible to predict an ultimate failure date as there are just too many variables. Sure the copper should last thousands of years but the insulation has no millenia of data to show its mean failure.

Sparky from your post I am assuming that you don't know that arc fault breakers have ground fault protection built in. It is not GFCI protection and trips around 30 milliamps instead of the 6 MA for GFCI protection.

Posted By: homerjones Re: old knob and toob wire - 01/06/10 06:22 AM
JUST MY 2 CENTS. BUT TELL THE CUSTOMER IT NEEDS A TOTAL REWIRE. IF THEY DON'T WANT TO PAY, WALK AWAY. I'VE WORKED FOR MICKEY MOUSE CONTRACTOR'S WHO ARE WILLING TO PUT IN OLD USED BULLDOG BREAKERS IN A RELIC PANEL AS AN EXAMPLE. I USED TO SAY, TELL THE CUSTOMER THEY DON'T EXIST. I WOULD'NT EVEN KEEP THAT OLD GARBAGE AROUND MY SHOP IF I HAD ONE, NOT WORTH THE HEADACHES.
Posted By: leland Re: old knob and toob wire - 01/06/10 07:35 AM
I SEE K&T that has been in use for 80+ years in better shape than NM in use for 20 yrs.

Most damage is at the devices. Where exposed to all that deadly O2.
(That Mr. Gore wants to out law) (OOPS)
However,I do recommend it to be -Upgraded- Not changed- Unless serious issues are found.

Most issues 'Needs' can be addressed with a service upgrade or new ckts to an already upgraded service.

Most N&T I see,is in better shape than the added stuff.
Posted By: sparky Re: old knob and toob wire - 01/06/10 04:05 PM
Quote
Sparky from your post I am assuming that you don't know that arc fault breakers have ground fault protection built in. It is not GFCI protection and trips around 30 milliamps instead of the 6 MA for GFCI protection.


well i believe that would make it a GFPE here MikeS, and no, nobody really knows all the parameters of the AFCI.

but that's really inconsequential , given the situation i have repeatedly stepped into around my turf , the insurance companies are dictating what is, and what is not 'safe' wiring, at least in that limbo term 'existing' is applicable

i've approached some, or suggested my customers approach them, with the idea of installing afci's

explaining that it stands for 'Arc Fault' and that one can contact the manufacturer for details

The onus of credibility is then, shifted bettween these entities , they decide, not me.

and why shouldn't it? any AHJ can ask me here to produce manufactuer's information on any electrical item i install, i've just kicked it all upstairs to where the real movers and shakers are

I've explained this to the local AHJ too. He's conceeded to my methods as the bandaid that it is. About ten years ago i also wrote UL asking the same Q, but they did not forward a detailed reply.

In an economy where few have the $$$ for a complete rewire, and a biz can get shut down , or a homeower rejected by the insurance cabal , any sanctioned avenue is going to be investigated

my methods from this point are typical, usually done in stages. 1)split up the older larger circuits into a number of derated ones, 2) investigate & reterminate with plastic enclosures (not metal) 3)provide new dedicated circuitry where applicable 4)GFCI at point of use where required.

so they eventually get a rewire anyways....

~S~



Posted By: mikesh Re: old knob and toob wire - 01/06/10 07:46 PM
Sparky
I like that "Insurance Cabal". The are selling insurance but it is poor business to sell only to the high risk guys. Actuarial data indicates that most house fire are in houses older than 40 years. I can't comment on what data they use to determine risk but if it motivates people to at least visit the current state of their electrical systems, then I am on their side. It also makes for more work for us, also good. My experience indicates that it is actually removing a lot of the abused wiring around town. Sure there are a few Little old ladies that have never blown a fuse and are living in the same house for 60 years. Never a home handyman or contractor has ever altered or damaged the wiring. I still have a couple of 120 volt 30 amp services here just waiting for a change of ownership to get an insurance upgrade. Nothing lasts forever and with only a hundred years of electricity in houses there are still a lot of risks that have not been measured yet. Code books don't make rules for upgrade except for a couple of rules in section 2 that speak to maintenance.
Posted By: sparky Re: old knob and toob wire - 01/08/10 02:05 AM
Actually i'm probably being too hard on the insurance industry Mikes, hard not to being a contractor.

In this case, you've a point in that they really are the only game in town pointing out what is obvious to us in our trade, yet oblivious to much of the general public....

Especially in those catch 22 'existing' situations, which i tend to stumble into more than i really care to

~S~
Posted By: Sixer Re: old knob and toob wire - 01/26/10 07:30 AM
You guys have posted some valid arguments regarding K&T.

In my neck of the woods, when a house with K&T gets sold, the insurance companies want the new homeowner to have an EC come in and sign their life away stating that the K&T is "safe", or have it replaced.

Obviously, the insurance companies feel that there is a risk factor when knob and tube is involved. I'm sure those risk factors are based on other claims where the wiring failed, otherwise it wouldn't be an issue.

Posted By: renosteinke Re: old knob and toob wire - 01/26/10 05:18 PM
I remember reading an Ontario report that took an in-depth look at knob & tube wiring. The report confirmed what I had always suspected: it's not the wiring method itself that's the cause for concern.

Instead, the study found all manner of problems with circuit 'improvements' and other consequences of an overall inadequate system.

The most obvious was degraded insulation, due to either overfusing or simply putting too large a bulb in the fixtures.

Then there were the three-prong receptacles on circuits without an equipment ground.

Naturally, it was fairly common for some romex to be spliced into the system, usually to add outlets or as an easy way to bring power to a remodel. Apart from the ground wire question, there was the manner of splicing.

Covering K&T with insulatio was so common as to be the 'norm.'

The issue isn't with 'knob & tube' per se. I've seen houses with perfectly fine K&T. The problem is that our lives typically require a lot more power than they did in the 40s, and the basic electrical design of the residence is
no longer adequate.

As an example, my place in Reno was perfectly happy being served by 30 amps and two circuits - for the entire place. Were I to rebuild that same place today, code would require a 100 amp service and at least five circuits; a sparky would likely up that circuit count to a dozen.

In a like manner, the place was wired with but four duplex receptacles and two single receptacles. If built under today's rules, that same house would require at least 16 receptacles (and the sparky would likely install 21, all but one duplex.

Associated with the K&T is the issue of the service; while it's another topic, there's a much greater push to replace the fusebox with a modern breaker panel.
Posted By: uksparx Re: old knob and toob wire - 01/29/10 08:34 PM
We never had knob and tube here in the UK, but have similar issues with old properties that retain the vulcanised rubber insulated, lead sheathed cables.They were never designed with today's demand in mind and get "butchered" joints added too. Plus, you need some skill to ensure the earth (ground) continuity of the metallic sheath. Thankfully there are not too many of these installs left, but they are still there.