I say: VIOLATION, big time!

They want to claim that each drop is allowed to have six meters without needing a disconnect? I'm not buying that - I'd expect to see, at minimum, four disconnects, each feeding six meters.

Better yet would be a single disconnect, feeding meter stacks, with the appropriate bussbars. (I'd really, really hate to try to split off 24 meters from one wire using split bolts!) Or, it might be a use for those new full-current rated insulation-piercing connectors; after all, you'd be tapping down from BFW-mcm to tiny #3 laugh

(Moderators' Note: BFW = Big Fat Wire)

I also have problems with different drops going into the same gutter.

I am simply stunned that the PoCo allowed this.