Okay gang- I rarely see a permanently installed swimming pool that is installed above ground. Here's the picture, vinyl liner, and steel wall with support members around the perimeter. The question that come up is: do I need a "Perimeter Surface grid" extending out 3 feet from the pool. If I do, what would be acceptable? If I understand correctly, and that might be the problem, the purpose of the perimeter surface grid is for the people setting on the edge of the pool and dangling their feet in the water exposing their bod to a difference of potential. Pretty hard to do with an above ground pool.

Greg- What do they do in the bikini State?

680.26(B)(2)