I have a couple of buck-boost transformers that I think are grossly undersized, and I'm hoping someone can check my math:
Two 3kVA, 600V, delta-connected auto-transformers should have a line current of 5 amps, correct?
3000VA * 2 * 0.87 (because it's an open delta) / 1.73 / 600V primary = 5.0A
Thanks a bunch.
-John
BigJohn.,
I came up complety diffrent number than your numbers.
Here is my verison.,,
3000VA X .87 ÷ 1.73 ÷ 600 = 2.51 amps
The 1.73 is allready taken care for triphase { it dont matter if open delta or close delta or wye format }
But just wondering why you add X 2 in there so if you try that again like my formaila and also I did used the electrician caluacator to see and the answer and it came pretty close it show 2.8amps on that one.
Merci,Marc