I am looking for opinions on the electrical work that was installed on a project that I am reviewing for code issues.
Thanks,
Bill A.
![[Linked Image from electrical-photos.com]](https://www.electrical-photos.com/data/506/medium/Electrical_Room_Picture_3_Ceiling_Area.jpg)
for the first photo there is lack of support of the MC's and I don't think it will fly very well in some area.
Then again in second photo the same issue not engouh support there and also with looks like 10X10X6 3R box there did someone screw up with MC mesurement ?
on Third photo either I am missing something but is that black wrap is legit type of materal to use to hold the MC's and also the distance from upper support to lower support or breaker box is a mite too far apart?

What up with that?? few tight bends with MC cables and where is support from the floor to breaker box to the left ?

It will be alot neater and quicker if ran few 1 or 1.5 inch conduits between breaker box and " splice box "
Now for last photo I don't what to say here if this is a real EGC it should be irrevsbale compression fitting or cadweld it.
useing the water pipe bonding clamp do not fly either side of pond anyway.
Merci,Marc