From a practical sense, as long as everything is GFCI protected, this will not present many real hazards. I think I would follow John's lead. Just how temporary is this. If it is a one day event I think you can skip the ground rod. How are they protecting the feeder and the branch circuits on the line side of the GFCI? That is your hazard zone.