Originally Posted by JBD
Originally Posted by richxtlc
PPE is required for voltage testing, i.e., "00" or "0" voltage rated gloves with leather protectors, plus voltage rated test equipment. This also means the proper category. CAT I, II, III, IV. The closer to the utility source the higher the category instrument required for safe testing.
See NFPA 70E Table 130.7(9)(a) for Panel Board Rated at 240V and Below for PPE required.


If an arc flash study has not been performed then voltage testing PPE also requires a Hooded Face Shield. The task tables show this as 2*.

I believe with the next edition of NFPA 70E, face shields will be required for all testing with hand held meters.


Niether of these statements are true, the PPE requirements depend on the charteristics of the system you are working on.

The only change in 2008 regarding facesheilds will be allowing a arc rated facesheild with Balakava to be used in place of the switching hood for HRC 2* tasks.

Last edited by Zog; 02/29/08 10:02 PM. Reason: Forgot to add quote

MV/HV Testing Specialist, "BKRMAN"