Don Gotta be at least a 3/0. 250.66 says a service this size requires a 3/0 ground Minumin. 250.24 (C) 1 says Neutral cannot be smaller then grounding electrode conductor per 250.66. Thats where I came up with the 3/0. 1/0 is Min. size under 310.4 for Paralling conductors. Yoopers