250.24(C)(2)applies to this installation. You install the larger of what is required by the Article 220 load calculation or 250.24(C)(2). 250.24(C)(2) would require a 1/0 in each of the 8 raceways and as long as the load calculation shows less than 1040 amps for the neutral you are good to go.
Don
Don(resqcapt19)