I have worked with medium/high voltage for more than 30 years in the utility industry and for the past few years in the commercial sector. As stated by several people, work at this voltage level requires special training and procedures, including specialized test equipment. OSHA 1910.333(b)(2)(ii)(C)and .333 (b)(2)(iv)[A]and [B} both determine how high energy circuits should be handled. It states handling of capacitors or other high capacitive elements, but if you have ever worked with medium voltage before then you know that the meter sometimes bounces when contact is made indicating a stored charge on the bus.
In addition to the OSHA reference, NFPA-70E 120.1 also refers to grounding when the possibility of induced or stored energy exists.
Although NFPA-70E was not included in this years OSHA update, it can still be used under the General Duty clause of OSHA in a legal case., The record of success when interperting the General Duty clause when failure to apply the provisions of 70E to a given situation is referenced is close to 100%.