Not having the read the new article I am limited in my ability to comment upon it intelligently.

That being said however....what is wrong with requireing GFCI protection for drinking fountains? I have been at this a while and can remember three specific instances where I did calls that involved energized fountains. While no one died or was seriously harmed, in principle they could have been.

Sort of reminds me of the resturant kitchens I have been to where they warned you that the cooler/freezer would shock you if you touched it while grounded. Yet they continued to use them and only mentioned it as ancillary to the reason I was there on a call.

Chilled water drinking fountains contain both a compressor and a condensor, a condensate tray often with electric heat, and other sometimes electrically powered controls. They also are subject to vibration because of the compressor which could lead to cable wear and fatigue at terminals.

Once upon a time when all drinking fountains were connected rigidly to both a metallic supply and metallic drain both of which were grounded these concerns had no merit. Any fault within the appliance would constitute a ground fault sufficent to trip the branch circuit breaker. This is no longer true however.

You may continue to enforce the code with a straight face, drinking fountains are exactly the type of appliance that can benefit from GFCI protection.