Electric-Ed,

If the grounding electrode conductor in diagram two is bonded to both the generator frame (and the generator neutral) as well as the service neutral (at bonding jumper), what is opening the neutral accomplishing?

Would seperate electrodes (and conductors) be better?

(I'm following the blue line representing the EGCs)

It just doesn't seem to be isolating the noodles at all to me...

[Linked Image]

Other than that, I'm glad that I've actually been putting them in right!


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI