This guy said he has no bad voltages. The neutral connections are therefore OK. Like Joe said, he has paralleled the neutral with the equipment ground.

Look for a connection from neutral to ground somewhere other than at the service. Probably one or all of the subpanels. The neutrals and grounds should all be separated, never to touch, except at the service.


Earl