The wording in the Code is similar to NEC for pendant lights, but there's a part that prohibits many of the light installations of this variety by a somewhat left-handed means. It limits the mounting height to no lower than a minimum of 7 ft 6 in. above the maximum water level. Even then they require a ground-fault circuit interrupter for it.

You can use recessed fixtures with a glass or plastic lens and nonmetallic or electrically isolated metal trim, suitable for use in damp locations or surface-mounted fixtures with a glass or plastic globe and a nonmetallic body or a metallic body isolated from contact if the fixtures are suitable for use in damp locations lower than the 7'-6 above the maximum water level if you provide a ground-fault circuit interrupter.

To paraphrase the Chicago Code; "sure it's okay...just jump through this moving hoop while whistling Dixie and juggling these oranges".

They're very accomodating here.


Ghost307