Originally Posted by ShockMe77
Say I had (3) 277 volt circuits and the load was 10, 4-lamp, 2x4 lay-in fluorescent light fixtures for each circuit, could I run a 12/4 MWBC and share the neutral for all three circuits?


yep you can do that that is very common on commercal area