Here is part of the installation instructions from the PostGlover website. They are a manufacturer of hospital isolated power systems.
Quote
All Branch Circuit Conductors of the isolated power system shall be stranded copper having a cross-linked polyethylene insulation, or equivalent with a dielectric constant of 3.5 or less. Type XHHW is suitable for this purpose. Each branch circuit conductor shall be color-coded in accordance with National Electrical Code. Wire pulling compound produces an adverse effect upon the dielectric constant of conductor insulation and shall not be used when pulling the wire of the isolated power system. Use of dry talcum powder is permitted.

PostGlover Isolated Power Panel
Don



[This message has been edited by resqcapt19 (edited 10-24-2002).]


Don(resqcapt19)