Wow!,
What a discussion is going on here!.
Keep it up guys.
Don,
Many utilities give you a "worst case" fault current, which will always let you select equipment that will be in compliance with the NEC, but may lead to the selection of arc flash PPE that is not suitable for the incident energy.
Utilities like the one that I work for always give what we call a "maximum-fault-loop current" to the point at which you are working.
However, with working with this sort of stuff all the time, I carry a "Fault-Loop Impedance meter", from getting that value from the meter, you can work out through basic Ohms Law, what the actual Fault current value will be.
The main rule is that you do not work anything hot except for troubleshooting. The main use of the PPE will be when you verify that the power is off after locking it out. Under the safety rules, you must assume that it is still live until tested with a voltage tester. You are exposed to the live equipment when testing for voltage and PPE is required.
I couldn't disparage anything in that comment.
Half the problem is, when people just disregard the rules and work however they please.
This in itself, needs to be corrected.