Gidday Alan, I use an AVO Megger Installation tester to do my testing of RCD's. I have seen these results pop up everytime I test. Over here it has to be under 300mS trip time at the stated (say 30mA) current. I think the longest time I have had is 42mS, and that was at 300mA, with a Selective RCD.