If you bundle 10 to 20 current carrying conductors, the derating factor is 50%. If you have no more than 6 outlets at 180 VA each on the circuit, you would still be OK for derating with out increasing the size of the conductors (assuming #12 wire and 20A circuit).
Reference:
310.15(B)(2)(a)
Note: EGC's and Multiwire "true" neutrals are exempt from the conductor count.
<disclaimer> This is how I interpret it. </disclaimer>