Trumpy,
3-phase Gen sets should have their star points connected to earth. 1p sets should have one pole connected to earth. The connection should not exceed 10ohms. Wiring then proceeds as standard with the gen set earth connected to the installations earth terminal. Some people use the smaller sets without reference earth but these should generally be restricted to single circuit applications.


regards

lyle dunn