From the 2002 National Electrical Code:
210.50 General. Receptacle outlets shall be installed as specified in 210.52 through 210.63.
(C) Appliance outlets. Appliance receptacle outlets installed in a dwelling unit for specific appliances, such as laundry equipment, shall be installed within 1.8m (6 ft) of the intended location of the appliance.
210.52 Dwelling Unit Receptacle Outlets. {.....} Receptacle outlets required by this section shall be in addition to any receptacle that is part of a luminaire (lighting fixture) or appliance, located within cabinets or cupboards, or located more than 1.7m (5-1/2 ft) above the floor.
(A) General Provisions. In every kitchen, family room, dining room, living room, parlor, library, den, sunroom, bedroom, recreation room, or similar room or area of dwelling units, receptacle outlets shall be installed in accordance with the general provisions specified in 210.52(A)(1) through (A)(3).
(1) Spacing. Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 1.8m (6 ft) from a receptacle outlet.
(2) Wall Space. As used in this section, a wall space shall include the following:
(1) Any space 600mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways, fireplaces, and similar openings.
(3) Floor Receptacles. Receptacle outlets in floors shall not be counted as part of the required number of receptacle outlets unless located within 450mm (18 in.) of the wall.
(C) Countertops. In kitchens and dining rooms of dwelling units, receptacle outlets for counter spaces shall be installed in accordance with 210.52(C)(1) through (5).
(1) Wall Counter Spaces. A receptacle outlet shall be installed at each wall counter space that is 300mm (12 in.) or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 600mm (24 in.) measured horizontally from a receptacle outlet in that space.
(D) Bathrooms. In dwelling units, at least one wall receptacle outlet shall be installed in bathrooms within 900mm (3 ft) of the outside edge of each basin. The rece[tacle outlet shall be located on a wall or partition that is adjacent to the basin or basin countertop.
(E) Outdoor Outlets. For a one-family dwelling and each unit of a two-family dwelling that is at grade level, at least one receptacle outlet accessible at grade level and not more than 2m (6-1/2 ft) above grade shall be installed at the front and back of the dwelling. {.....}
(F) Laundry Areas. In dwelling units, at least one receptacle outlet shall be installed for the laundry. {.....}
(G) Basements and Garages, For a one-family dwelling, at least one receptacle outlet, in addition to any provided for laundry equipment, shall be installed in each basement and in each attached garage, and in each detached garage with electric power. {.....}
(H) Hallways. In dwelling units, hallways of 3.0m (10 ft) or more in length shall have at least one receptacle outlet. {.....}
That's a somewhat edited summary, but I think it gives a fair picture. I'm sure one of our American friends will add anything important that I've overlooked.