Bob,
Quote

Not in a panel.

Derating only applies to raceways or cables.

Are you sure???

Quote
310.15(B)(2) Adjustment Factors
(a)More Than Three Current-Carrying Conductors in a Raceway or Cable. Where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing and are not installed in raceways, the allowable ampacity of each conductor shall be reduced as shown in Table 310.15(B)(2)(a). Each current-carrying conductor of a paralleled set of conductors shall be counted as a current-carrying conductor.

Don
edited to fix code for quote

[This message has been edited by resqcapt19 (edited 02-27-2006).]


Don(resqcapt19)