Are the tables fastened in place? That would be a violation of the 30 x 36 inch clearnces wouldn't it?

The code section is 110.26(A) however renosteinke had stated there is a work space violation.

I do want to point out that if the tables are fastened in place or not does not make any difference.

The working space is required to be kept clear by 110.26(B)


Bob Badger