This is my first submission.

I have a maintenance agreement for a local townhome community. Got a call for a breaker trippping. No heat. Investigate and find a smoking Sylvania 2 pole 60a for the heat pump.The breaker overheated enough to melt the buss bar. So off to the supply house to get a new panel and cable *** panel recessed in the wall and 150a main*** 4 hours later im finished.(i think). I turn it on test everything and im on my way home. I live 3 miles away and dont even get home and i get a call on the cell " there's something smoking under the steps" The disconnect in the picture turned out to be under the steps and all kinds of junk piled in front of it. Not in sight of the heat pump it controls. NOW THE FUN PART 30a disco(60a heat pump) 3 pole disco (note the 2 hots and the ground on the terminals) . (Not bonded). The unit was installed 2 years ago by a heating contractor!!!
A simple job turned into a nightmare.

God i hate heating contractors that think they are electricians.