GAapprentice,

The wire connectors are not against code at all, as long as they don't fill more than 75 % of the cross-sectional area of the panelboard. See 312.8 of the 2002 NEC. That does not appear to be a problem in this picture.

An inspector may not like to see the wirenuts, but there's nothing he can do about it. [Linked Image]


Peter