Erik,

These terms are really referring to the use to which a transformer is put rather than the way it operates. All transformers follow the same basic laws of physics and work the same way.

There are differences between them in construction though, dictated by the functions they need to perform. A xfmr designed as a CT to monitor current remotely has a primary which might be just a solid busbar passing through it -- basically a 1-turn primary.

On the other hand, a xfmr used to monitor voltage remotely on a line will have a primary with many hundreds or thousands of turns so as to keep the current it draws low. The secondary will then have fewer turns so as to provide a low voltage output.

If you take the xfmrs calculations you were looking at a week or two ago, you'll recall the basic formula:

Np / Ns = Ep / Es

In other words, the ratio of primary turns to secondary turns is the same as the ratio of primary voltage to secondary voltage (in a perfect xfmr!).

In general electrical usage, a CT will have Ns much greater than Np. A voltage xfmr, where used to remotely monitor high voltages, will have Ns much smaller than Np.

Remember though, that you can't change one without the other:

Np / Ns = Is / Ip

So a current xfmr used to reduce the current to a level suitable for measurement will also step-up the voltage. (We're not talking about the supply voltage level on the system being monitored, we're talking about just the very small voltage drop on the "single-turn" of the busbar as it passes through the CT).

Similarly, where a xfmr is used to reduce voltage to a safe level for remote monitoring, the current in the secondary (Is) will have to be correspondingly greater than that flowing in the primary (Ip).