I saw that question and I believe the editor of the CQD missed the point of the question. He responded, correctly, with regard to ampacity. However, I think the question pertains to whether or not a CB is required at the supply end. Even if the questioner follows the inspectors directive by installing a CB at the supply end, the ampacity problem still exists. According to 310.15(6),the additional allowable ampacity for #2 al conductors is only where they are used as service entrance conductors, or where used as the main power feeder to a dwelling.