Question:
We installed a 200-ampere service in a home. The service panel is
rated 200 amperes and equipped with a 200-ampere main breaker. The
panel has sub-feed lugs at the bottom and we used these lugs to feed a
panel 20 feet away with 2 AWG AL conductors. These conductors
terminate in a 100-ampere main breaker in the second panel. The
inspector required us to put a 100-ampere breaker in the service panel
to feed these conductors citing 240-3 (1999 NEC). Is he correct?
Answer:
Section 240.4 (2002 NEC) reads the same as 240.3 (1999 NEC). This
section requires that conductors be protected against overcurrent in
accordance with their ampacities <b>unless</b> otherwise permitted in
240.4(A) through (G). Section 240.4(E) permits tap conductors to be
protected against overcurrent in accordance with 240.21.
Section 240.21(B)(2) permits tap conductors not over 25 feet long to
be run without overcurrent protection at the source if all of the
provisions of 240.21(B)(2) are complied with. Your installation
complied with (1) where the ampacity of the tap conductors is not less
than one-third of the rating of the overcurrent device protecting the
feeders (200A), and (3) where the tap conductors are suitably protected
from physical damage or are enclosed in a raceway. However, (2) that
requires tap conductors to terminate in a single overcurrent device
that limits the load to the ampacity of the tap conductors was not
complied with, since the ampacity of 2 AWG AL as shown in Table 310.16
is 90-amperes.
You may be using the 90ºC column where 2 AWG AL is rated at 100
amperes but this isn't permitted because the terminations in your
panels aren't rated 90ºC. You may be using Table 310.15(B)(6) where 2
AWG AL is rated at 100 amperes but this table only applies to
service-entrance conductors and feeder conductors that serve as the
main power feeder to a dwelling unit.
Since 240.6 shows a 90-ampere circuit breaker as being a standard
size, you must change the 100-ampere breaker to a 90-ampere breaker to
be in compliance with the NEC.