Big Guy

If you look around this site you will find pictures of my work.

Yes I have run jobs that I would not want to show pictures of here, not every job is pretty.

Quote
After looking again at the pic,s I don't see no live wire's on the floor.

Picture 1 the bundle of yellow stuff coming out of the panel, running across the floor is wire and it is live.

NM cable even when used for temps is not hard usage cord.


Quote
The romax is ok for temp

Yes, I use it for temps all the time.

Quote
and does not need to be staped as often in the ceiling

Can you show me a code that says that?

The NM in the trusses is not temp it is permanent, it is required to be supported every 4.5'.

Quote
Why don't you tell this guy that there is pic's on the net of his job?


I have no idea who he or she is.

Quote
It is not fair that the job is not done and you are cutting this guy up with know Idea of what is going on.

I am willing to go out on a limb and assume that this job is not going to suddenly clean up. I do have a pretty good idea of what is going on and the diffacult job they have here. They are trying to do a major remodel without disrupting the store.

I have run jobs like that and it is very hard, so what, you still have to follow the rules.

Quote
How can you or anybody say anything with out being there on the job working on this project with the guy doing it

There is absolutely no excuse for using cardboard to cover 480 busbars. This is dangerous, irresponsible and would be a major issue if OSHA shows up.

Quote
Maybe he can take some pic's of your jobs before it is all done.

People take pictures of my jobs often, GCs engineers, owners representatives. And while they may not always be perfect you will never see my jobs looking like this one.

Quote
Keep running everybody else down your doing a good job

I am sorry you feel that way, I must assume you have not read many of my posts.