I dont't think 408.20 (408.40 in '05)has been violated here. There are terminal bars installed they just have not been used. When used as service equipment the unused terminals in the "neutral bars" (my term) can be used to terminate equipment grounding conductors. No need to install addtional "ground bars" unless you run out of terminals. I think the splitbolt is a violation and I suspect that the trough is over filled. Basically a hack job.