Gwz,

1956 NEC 4113 is todays 2002 NEC 410.6.

Quote
410.6 Luminaires (Fixtures) Over Combustible Material.
Lampholders installed over highly combustible material shall be of the unswitched type. Unless an individual switch is provided for each luminaire (fixture), lampholders shall be located at least 2.5 m (8 ft) above the floor or shall be located or guarded so that the lamps cannot be readily removed or damaged.
NEC Handbook commentary:
Quote
Section 410.6 refers to pendants and fixed lighting equipment installed above highly combustible material. If the lamp cannot be located out of reach, the requirement can be met by equipping the lamp with a suitable guard. Section 410.6 does not apply to portable lamps.
I find the section use of "lampholder" while pointing to "luminaire" interesting.

[This message has been edited by ElectricAL (edited 02-07-2003).]


Al Hildenbrand