Joe,

I always enjoy your code violations column in here and in EC&M and since I've seen a few myself I thought I'd send one in for you to add to your collection.

I only wish I had a better picture for you!

Whenever you research an industrial facility for a system re-design you generally come across some questionable installations.

During one several years back I stumbled across this unique one.

Although difficult to count, this 600 V - 100 A breaker had approximately fourteen (14) separate conductors ranging from #14 to #2 AWG under each load side lug.

Each conductor ran a considerable distance feeding separate devices.

Do you suppose this would be considered a code violation?

This situation has since been corrected as part of the system re-design.

Dennis T. Croughwell
Mgr - Central Maintenance & Facilities Services


Joe Tedesco, NEC Consultant