Ok,,,,there are a few things here to address.
First lets start with your EC,
HE is the one responsible for notification to the AHJ .
2nd . as a rule I don not acccept request from GC's for inspections ( don't get mad yet)
80.19 (F)(1) Upon completion of any installation of electrical equipment that has been made under a permit other than an annual permit, it SHALL BE the duty of the person, firm or corporation making the installation to notify the electrical inspector having jurisdiction , who shall inspect the work within a reasonable time .
( see rule 10 below )

However , there are times and this might be one , where I would go , but with the understanding if it failed , an extra fee would be assesed and untill it was fixed you would have to wait, this would not make for a happy AHJ if the electrician tells him he wasn't ready to begin with.

3rd I would like to know what the Bldg Inspector had to say about this.

the local authority over the AJH would be him or the town manager or council.

what to do ?

1 . hire a new EC have him pull a new permit
2. send a notifacation of termination of the old EC along with a notice for inspection .
certified mail !
after that 527 CMR 12.00 (MEC Amendment)
Rule 10.. says,
Electrical installations shall not be concealed or covered from veiw until inspected by the inspector of wires within and not more than 24 hours for exterior excavations nor more than 72 hours for interior installations after proper
to the Inspector.
saturdays and sundays and holidays excluded


All that being said
remember..willthis be the only job you'll will ever do in this town?
don't set fire to a bridge you might need to cross someother time.
the town of clinton has more bars per capita than anyother town in mass,,,buy the guy a beer!!!even if he doesn't accept be nice about it

the later is my advise..good luck

HV

[This message has been edited by HIGHVOLTAGE (edited 05-31-2002).]