George,
Quote
I wonder what your thinking is about the horsepower thing?
440.12(A) does not require a horsepower rating for this disconenct. As long as the ampere rating of the disconnect is equal to to or greater than the branch circuit selection current you are in compliance.
Don


Don(resqcapt19)