I recently did a service that someone else started where I had to relocate the service head. I used 250 kcmil from POCO service drop to a 320 amp rated meter. From out of the meter there were two sets of feeders, each going to 200 amp main breaker panels fed with 2/0 copper. So this is considered a 300 amp service based on the size of the feeders going to the POCO drop. Correct?
Could someone tell me what article permits using (2) 200 MB panels for a 300 amp service?
#2 copper was run to H20 meter and #4 copper was run for the Ufer. Also, #2 jumper was installed to bond both ground busses in either panel.