I see no problem with this arangment and as far as the recptical goes it can be eather a gfci breaker or recptical. if he intends to leave to bug lamp pluged in permently you need to install a cover thats rated for this type of use. it has to be rain tight while in use. also use a 4 wire run to the panel because neutrals and grounds must be kept seprate after main meens of disconect which is back in the cuttler hammer panel.
:Wayne

680-12. Disconnecting Means
A disconnecting means shall be provided and be accessible, located within sight from all pools, spas, and hot tub equipment, and shall be located at least 5 ft (1.52 m) from the inside walls of the pool, spa, or hot tub.

680-40. Outdoor Installations
A spa or hot tub installed outdoors shall comply with the provisions of Parts A and B of this article except as permitted in (a) and (b).
(a) Flexible Connections. Listed packaged units utilizing a factory-installed remote panelboard shall be permitted to be connected with not more than 6 ft (1.828 m) of liquidtight flexible conduit or be cord and plug connected with a cord not longer than 15 ft (4.57 m) if protected by a ground-fault circuit interrupter.
(b) Bonding. Bonding by metal-to-metal mounting on a common frame or base shall be permitted. The metal bands or hoops used to secure wooden staves shall not be required to be bonded as required in Section 680-22.

[This message has been edited by hurk27 (edited 05-27-2002).]