428
15
Does this identification look OK?
O.K. I'll be the fist one to bite, It looks good to me. Am I missing something?
It looks like everything in 240.83 has been satisfied.
Ryan Jackson, Salt Lake City
Posts: 2,723 Likes: 1
Broom Pusher and Member
Looks like a 2 Pole frame, with no handle tie across the reset handles.
If this is a 2 Pole unit, then the following would be identification issues:
<OL TYPE=1>
[*] Listed as a 1 Pole unit on both Poles of the unit,
[*] No common trip indication. </OL>
Scott35
Looks OK to me, although Ryan brings up a good point, on 240.81
So you're saying that the problem isn't in the identification at all, but in the text that was added to the photo?
I figured you were talking about code compliance with the breaker itself, not the added text.