Does this identification look OK?
[Linked Image from nachi.org]
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
O.K. I'll be the fist one to bite, It looks good to me. Am I missing something?
It looks like everything in 240.83 has been satisfied.
Ryan Jackson,
Salt Lake City
But what about 240.81?
Ryan Jackson,
Salt Lake City
Broom Pusher and
Looks like a 2 Pole frame, with no handle tie across the reset handles.
If this is a 2 Pole unit, then the following would be identification issues:
<OL TYPE=1>
[*] Listed as a 1 Pole unit on both Poles of the unit,
[*] No common trip indication.
</OL>
Scott35
Scott " 35 " Thompson
e57 Offline
Looks OK to me, although Ryan brings up a good point, on 240.81
I cropped the image to get a close up and here is the rest of the story.
Note: UL does not approve they list or label and the CSA I believe does the same.
http://www.nachi.org/bbsystem/usrimages/1/100_03031.JPG
http://www.nachi.org/bbsystem/usrimages/1/100_03041.JPG
So you're saying that the problem isn't in the identification at all, but in the text that was added to the photo?
Yup!
I figured you were talking about code compliance with the breaker itself, not the added text.
Ryan Jackson,