ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 265 guests, and 24 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 3 1 2 3
Joined: Oct 2000
Posts: 2,749
Member
Does this identification look OK?

[Linked Image from nachi.org]


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Dec 2004
Posts: 27
Member
O.K. I'll be the fist one to bite, It looks good to me. Am I missing something?

Joined: Aug 2003
Posts: 1,374
R
Moderator
It looks like everything in 240.83 has been satisfied.


Ryan Jackson,
Salt Lake City
Joined: Aug 2003
Posts: 1,374
R
Moderator
But what about 240.81?


Ryan Jackson,
Salt Lake City
Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
Looks like a 2 Pole frame, with no handle tie across the reset handles.

If this is a 2 Pole unit, then the following would be identification issues:

<OL TYPE=1>

[*] Listed as a 1 Pole unit on both Poles of the unit,


[*] No common trip indication.
</OL>

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
??????????????????????????????????????????????????????????????????????????????????????

Looks OK to me, although Ryan brings up a good point, on 240.81


Mark Heller
"Well - I oughta....." -Jackie Gleason
Joined: Oct 2000
Posts: 2,749
Member
I cropped the image to get a close up and here is the rest of the story.

Note: UL does not approve they list or label and the CSA I believe does the same.
http://www.nachi.org/bbsystem/usrimages/1/100_03031.JPG
http://www.nachi.org/bbsystem/usrimages/1/100_03041.JPG


Joe Tedesco, NEC Consultant
Joined: May 2005
Posts: 178
J
Member
So you're saying that the problem isn't in the identification at all, but in the text that was added to the photo?

Joined: Oct 2000
Posts: 2,749
Member
Yup!


Joe Tedesco, NEC Consultant
Joined: Aug 2003
Posts: 1,374
R
Moderator
I figured you were talking about code compliance with the breaker itself, not the added text.


Ryan Jackson,
Salt Lake City