makokiller
there is no code that says that you cant sleeve it first, and then put it in the ditch.
Actually there is a code rule that prevents that and I posted it above.
300.18 Raceway Installations.
(A) Complete Runs.
Raceways, other than busways or exposed raceways having hinged or removable covers, shall be installed complete between outlet, junction, or splicing points prior to the installation of conductors. Where required to facilitate the installation of utilization equipment, the raceway shall be permitted to be initially installed without a terminating connection at the equipment. Prewired raceway assemblies shall be permitted only where specifically permitted in this Code for the applicable wiring method.
Bob