Look at a 240 volt single phase circuit with an 80 amp load. To reduce the current by 16% you would have to reduce the I²R losses by more than 3000 watts at the termination. I really don't believe that a termination has 3000 watts of loss and if it does, it won't last very long before it melts down.
Don


Don(resqcapt19)