Thanks for the reply. It'll probably be cheaper for me, according to the exception of 680.23(F)(3) exception #1 , to put a GFI ahead of the feeder conductors so I can run the lighting wires through the same conduit. The column lights are around 10 or 12 feet or more, from the inside wall of the pool. Anybody every seen a 3 gang wp. switch box and cover?
Also if I read right, according to 680.23 (F)(2)exception (b), I can terminate the grounds for the two "in pool" lights on a grounding terminal inside the switch box that I will install the two switches in.
Remember these switches will be about 100ft. from the "pool pump panel". If I knew how to download a diagram I would show you what I'm talking about, but unfortunately, I don't and don't know if I have the proper port on my computer to do so. Any information on this would be appreciated also. Thanks a bunch ..Steve ...