Table 310.16 - Terminations #97117
01/23/06 10:12 PM
01/23/06 10:12 PM
R
rjr1950  Offline OP
Junior Member
Joined: Jan 2006
Posts: 2
Trophy Club, TX, USA
I was told that there are no wire terminations rated more than 75C degrees, and that this limits you to the temperature of the wire being used. Example - If I choose 2 aught THHN-2 from the table 310.16 the maximum ampacity would be 195 amps at 90C degrees, but because my termination was 75C degrees you would have to drop back to the 75C THHN conductor, which is rated at 175 amps. Is this correct?

2017 / 2014 NEC & Related Books and Study Guides
Re: Table 310.16 - Terminations #97118
01/24/06 01:05 AM
01/24/06 01:05 AM
B
Buck33k  Offline
Junior Member
Joined: Jun 2004
Posts: 6
Washington
There is a variety of mechanical lugs and neutral bars listed in the Ilsco catalog as 90 degree temperature rating.

Re: Table 310.16 - Terminations #97119
01/24/06 01:53 AM
01/24/06 01:53 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
You may have a little more trouble finding breakers and end use equipment with 90c terminations. You will be limited by the lowest rated termination on a conductor.

If you could start by using the 90c column there is no wiggle room for derating so the sharp pencil will come out.

Generally speaking you get limited at 75c.


Greg Fretwell
Re: Table 310.16 - Terminations #97120
01/24/06 04:07 AM
01/24/06 04:07 AM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
If you dont mind, what type of terminations are you trying to get for 2/0? Most insulated for a few years or so have been 90C, and I cant remember ever seeing non insulated with under 90C. Unless were talking apples and oranges? As gfretwell mentioned devices, breakers and such are a different story.

Take a look at 110.14C... I believe this is the code you're reffering to? Then 310.16, with ambient tempature correction factor. And 310.15 after that... The wire size could change some more? [Linked Image]
---------------------------------
Then a saving grace in 240.4B, via 240.6.



[This message has been edited by e57 (edited 01-24-2006).]


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Table 310.16 - Terminations #97121
01/24/06 09:00 AM
01/24/06 09:00 AM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Buck,

There is no UL Listed device termination rated at 90C. The rating of individual components such as a lug only is not the same as the overall rating of the device as required by 110.14(C).

I have always liked the Square D publication Wire Temperature Ratings and Terminations that discusses wires and terminations. "When terminations are inside equipment such as panelboards, motor control
centers, switchboards, enclosed circuit breakers, safety switches, etc., follow
the temperature rating identified on the equipment labeling instead of the rating
of the lug itself.

Re: Table 310.16 - Terminations #97122
01/24/06 10:36 AM
01/24/06 10:36 AM
G
George  Offline
Member
Joined: Feb 2002
Posts: 375
I am told that wire nuts are rated at 105 degrees.

So you run big wire from your equipment to a box using a wire nut change to a little wire. Do the same at the other end.

Poor practice but ...

Re: Table 310.16 - Terminations #97123
01/24/06 12:47 PM
01/24/06 12:47 PM
B
Buck33k  Offline
Junior Member
Joined: Jun 2004
Posts: 6
Washington
JBD
The SQ D publication was a good one. As you say, it makes clear there is no distribution or utilization equipment 600v or less listed 90C.
Also helpful for me was the reference included to 110.40, 90C above 600V.

Re: Table 310.16 - Terminations #97124
01/26/06 06:03 AM
01/26/06 06:03 AM
S
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 608
massachusetts
"I am told that wire nuts are rated at 105 degrees.
So you run big wire from your equipment to a box using a wire nut change to a little wire. Do the same at the other end.

Poor practice but ..."

George...Is this practice code compliant?

Would I have to increase the size of the EGC also as required by 250.122(B) for its entire length or just where the pigtails are tapped for device termination?

shortcircuit


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
Potseal 15
sparky 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,863 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 14 (0.004s) Memory: 0.9922 MB (Peak: 1.1509 MB) Zlib enabled. Server Time: 2018-01-22 22:17:22 UTC