#95537 - 09/20/05 10:40 AM Additional Ground Rod  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
When adding a grounding electrode to reach <25? when using a rod, is it permissible to for example, install a second acorn type clamp on the first rod and then run a piece of #6 copper to the second rod located at least 6 feet away from the first rod? The alternative would be to use only one clamp on the first rod and run through the clamp (uncut) to the second rod.


George Little

2017 / 2014 NEC & Related Books and Study Guides

#95538 - 09/20/05 12:52 PM Re: Additional Ground Rod  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
Yes, it is permitted.


Ryan Jackson,
Salt Lake City

#95539 - 09/20/05 01:25 PM Re: Additional Ground Rod  
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
Ryan
I thought the GEC had to be without splices except for specified connectors. I don't the the acron clamp was one of these clamps.


#95540 - 09/20/05 01:40 PM Re: Additional Ground Rod  
markp  Offline
Member
Joined: Apr 2004
Posts: 60
Kent, WA, USA
The GEC is the conductor from the Service Neutral to the Ground Electrode System (GES). The GES consists of all the various electrodes which are bonded together. At any one electrode is where the GEC stops. Past this, they are electrode bonding conductors and I don't see any splicing prohibitions on those.

The only thing you have to watch is when different size bonding wires are used. Lets say you have a #4 to a water pipe and then a #6 from there to two rods. You can't run a #4 GEC from the service to the rod because the bonding wire to the pipe is too small. Running a #4 GEC to the water pipe would be OK. Running a #4 GEC to the first rod would be OK as long as a #4 connects the first rod to the pipe. Even if there was a #6 from the first rod to the second this would still be OK.


Mark
Kent, WA

#95541 - 09/20/05 08:28 PM Re: Additional Ground Rod  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,853
Brick, NJ USA
George:
The issue around here was that second #6 was put under the acorn. It is listed for a single conductor only.

Mark:
I have never came accross an installation, as you described. It reads like you are running a #4 from the panel to the water pipe, and then a #6 to the ground rods????
I have never seen that, now I'll have to go get the bible!! WHAT DO YOU GUYS THINK??

John


John

#95542 - 09/20/05 08:31 PM Re: Additional Ground Rod  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I have had to do something similar several times. Since we are locally required to enclose the GEC in pipe, and the pipe/ ground rod connector does not allow for the wire to continue elsewhere, it is necessary to use an additional pipe/rod clamp, and run a separate pipe, with a separate wire, to the next ground rod.


#95543 - 09/20/05 11:06 PM Re: Additional Ground Rod  
dmattox  Offline
Member
Joined: Oct 2004
Posts: 265
Anaheim, CA
Quote

The issue around here was that second #6 was put under the acorn. It is listed for a single conductor only.


Simply put 2 acorns on the first ground rod and you are good to go.

250.62(F) is a powerful section that it seems like few people come to grips with. The handbook has a picture that clearly shows the ramifications of it.

Quote
To Electrode(s). A grounding electrode conductor shall be permitted to be run to any convenient grounding electode available in the grounding electrode system or to one or more grounding electrodes individually.


This allows both installations that George asks for, provided you use two connectors for the seperated GEC.

A little tip that this section allows is great for a large building. Say you have your switchgear near a building steel column. However your cold water is 500' across the warehouse which happens to be next to another building steel column. Simply bond your switch gear to the first column and bond the 2nd column to the cold water. Thus saving 500' of GEC.

One catch, engineers will often exceed NEC requirements and require seperate conductors. But, that is not required per the NEC.


#95544 - 09/21/05 05:55 AM Re: Additional Ground Rod  
Happy Birthday iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Morning John

Quote

I have never came accross an installation, as you described. It reads like you are running a #4 from the panel to the water pipe, and then a #6 to the ground rods????
I have never seen that, now I'll have to go get the bible!! WHAT DO YOU GUYS THINK??


I think it is fine.

I have gone from a large service to building steel then 200' - 250' across the building I jumped from building steel to water service saving the long run of 3/0 between the water line and the service.

Here is a Handbook image that shows some possibilities.

[Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#95545 - 09/21/05 11:47 AM Re: Additional Ground Rod  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,099
Estero,Fl,usa
OK how about if the electrode in question is a Ufer. I pick it up at the service disconnect and 300' away I find another piece of turned up Rebar, can I bond my water to that?


Greg Fretwell

#95546 - 09/21/05 01:38 PM Re: Additional Ground Rod  
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
Based on the discussion and the image above, if the turned up rebar is closest to the water, I don't see any reason not to use it.

If any portion of the water is nearer to the service, then AHJ would probably say no.


Stupid should be painful.

Page 1 of 3 1 2 3

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.078s Queries: 15 (0.064s) Memory: 0.8214 MB (Peak: 0.9993 MB) Zlib enabled. Server Time: 2017-07-21 22:47:40 UTC