480/277 panel feed with straight 480 #93197
05/06/05 09:31 AM
05/06/05 09:31 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
Can a 480/277 Sub panel be feed with straight 480 plus ground??? No neutral loads are required. All loads straight 480 v 3 phase.

2017 / 2014 NEC & Related Books and Study Guides
Re: 480/277 panel feed with straight 480 #93198
05/06/05 10:59 AM
05/06/05 10:59 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
Found my answer , (NO) 240.85 the breakers that fit in a 227/480 volt panel are rated 277 to ground and they must be rated 480 volt to ground incase the hookup feeding the panel is a 480 volt Delta not a Y.
Yoopersup

Re: 480/277 panel feed with straight 480 #93199
05/06/05 05:10 PM
05/06/05 05:10 PM
T
tkb  Offline
Member
Joined: Dec 2004
Posts: 94
Massachusetts
But the power will still be a Y system, just without the neutral connection.
It will still be 277 to ground unless you have a real 480 delta.
This is not uncommon in many industrial facilities.
I would just remove the neutral bar and re label the voltage on the panel.
Most likely would voilate the listing of the panel though. I would still be able to sleep at night though. [Linked Image]

Re: 480/277 panel feed with straight 480 #93200
05/08/05 05:27 PM
05/08/05 05:27 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
Not if fed with a True Delta secondary not a Y which is common in many Industral applications /

Re: 480/277 panel feed with straight 480 #93201
05/08/05 09:31 PM
05/08/05 09:31 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
tkb,
A 3 phase wye secondary without a connection to XO is an ungrounded system and would require 480 volt breakers. It only becomes 277v to ground when you bond XO. This system behaves exactly like an ungrounded delta and there is no way to tell the difference without looking at the transformer itself.
Don


Don(resqcapt19)
Re: 480/277 panel feed with straight 480 #93202
05/09/05 10:21 AM
05/09/05 10:21 AM
P
pdh  Offline
Member
Joined: Jan 2005
Posts: 354
Just to add to resqcapt19's post, a wye secondary could be bonded to ground at an end, such as X1, and then it would behave much like a corner grounded closed delta. That could be a suitable replacement transformer for an existing corner grounded delta system.

Now a question is, if the supply really is 480Y/277 at the source (X0 bonded), and the conductors brought to the panel are only X1,X2,X3 and G (not neutral), can you still safely and legally use 480/277 ratings? One thing you obviously cannot do is connect any 1-pole 277 volt loads. But 2-pole and 3-pole breakers (such as EDB series for Square-D NF panels) would be rated at 480/277 volts, so I would think they can be used even though the neutral is absent.

If this is an ungrounded or impedance grounded system, then it has to be treated as a pure 480 volt system since under a single-fault condition, it actually will be. And 240.85 limits 480/277 breakers to only solidy grounded systems with (not more than) 277 volts to ground. I assume Yoopersup's "straight 480 plus ground" could be a corner grounded delta where you cannot use 480/277 rated breakers (unless you know for sure otherwise, assume the worst). But can you use them if the system is definitely a 480Y/277 even if the neutral is not present?

Re: 480/277 panel feed with straight 480 #93203
05/09/05 02:18 PM
05/09/05 02:18 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Voltages ratings for panelboards are line->line and line->ground. The presence, or absence, of a grounded conductor is not germane. As long as the system is a solidly grounded wye the "slash" ratings of the equipment may be used.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 13
Popular Topics(Views)
243,542 Are you busy
180,344 Re: Forum
170,832 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9831 MB (Peak: 1.1357 MB) Zlib enabled. Server Time: 2018-01-19 01:45:32 UTC