#90826 - 12/12/04 06:24 PM Weired load calculation?  
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
How would you do load calculation for a single house that has 6 families living in it each with their own kitchen, laundry,...

Do I treat this as an apartment?

it is 6000 sqft house

Thanks
Edward


Thanks
Edward

2017 / 2014 NEC & Related Books and Study Guides

#90827 - 12/12/04 07:02 PM Re: Weired load calculation?  
rlc3854  Offline
Member
Joined: Sep 2004
Posts: 15
Amite, LA
Most building codes (IBC, UBC) will not allow this concept without applicable fire codes (state, county, city)being adhered to such as fire walls and seperate utlilities. Should there be only 1 poc for all utlilities you must perform load calucations under the NEC as each families area as being a seperate residence (IMHO).


#90828 - 12/13/04 12:14 AM Re: Weired load calculation?  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,099
Estero,Fl,usa
The only place I see as a problem is a possible lack of load diversity. You still count all of the small appliance circuits and laundry circuits at 1500va each. You might want to count all the stoves as the "first one". The other thing is the general lighting load. It would probably be overkill to put 3va on the whole 6000 feet but it is the safe call. Fixed in place equipment is the same. If it was close, you could probably round down to the next standard service size, assuming you took everything above on the high side.
Residential load calcs are just an educated guess anyway. You can have identical houses and one can routinely have twice the electric bill of his neighbor, simply ny lifestyle. Six families shacking up in a 6k ft house are probably on the cheap side anyway ;-)


Greg Fretwell


Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,260
Joined: December 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 14 (0.002s) Memory: 0.7520 MB (Peak: 0.8742 MB) Zlib enabled. Server Time: 2017-07-25 06:44:26 UTC