ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Photocell
by twh. 01/22/18 05:06 PM
AreMetal Ladders Ever OK For Electrical Work?
by gfretwell. 01/22/18 01:15 AM
VDE 0100 to introduce AFCIs
by sparky. 01/20/18 05:09 PM
MRI LED lights dimmer control replacement - wow!
by Potseal. 01/19/18 08:52 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 26 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Outdoor receptacle support #84916
05/16/03 10:24 AM
05/16/03 10:24 AM
B
bobwk  Offline OP
Junior Member
Joined: May 2003
Posts: 6
baltimore
Does an outdoor recptacle for commericial application, city streetscape, require any special mounting requirements. Can a GFCI in a weathproof box be supported 4" above grade by the two 2" pvc schedule 80 conduits that contain the branch circuit wiring? Does the NEC require device to be mounted to an independent board or pipe.

2017 / 2014 NEC & Related Books and Study Guides
Re: Outdoor receptacle support #84917
05/16/03 01:51 PM
05/16/03 01:51 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Bobwk:
The NEC does not allow a box to be supported only by conduits in most circumstances. I do not have the article handy at the moment.
THe box should be supported independently. We use strut,(stainless or epoxy paint coated) or a substantial (4x4) wood post.

Based on our experiences, landscapers, and the general public seem to "attack" GP receptacles, therefore we assure a minimal amount of callbacks by providing a substantial means of support.

BTW, there are some commercially available mounting methods that I saw in either EC Mag, or EC&M by Arlington, you may want to chekc them out.

My 2 cents,
John


John
Re: Outdoor receptacle support #84918
05/16/03 03:53 PM
05/16/03 03:53 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Quote
2002 NEC

314.23 Supports.

(F) Raceway Supported Enclosures, with Devices, Luminaires (Fixtures), or Lampholders.
An enclosure that contains a device(s) or supports a luminaire(s) [fixture(s)], lampholder, or other equipment and is supported by entering raceways shall not exceed 1650 cm3 (100 in.3) in size. It shall have threaded entries or have hubs identified for the purpose. It shall be supported by two or more conduits threaded wrenchtight into the enclosure or hubs. Each conduit shall be secured within 450 mm (18 in.) of the enclosure.


PVC is referred to in the code as Rigid Nonmetallic Conduit, so if you use two RNCs with male adapters into threaded hubs, you may well meet the code, but landscapers aim for stuff like this, IMO it will break, I would suggest using IMC or RMC for this.

Or do as hotline said and add a seperate support.

Just another opinion. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Outdoor receptacle support #84919
05/16/03 04:22 PM
05/16/03 04:22 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Bob,
I think that you could reject the use of PVC conduit to support the box because you are not screwing the conduit into the box. You are screwing the male adapter which is connected to the conduit into the box. The section clearly requires that the conduit be screwed into the box.
Don


Don(resqcapt19)
Re: Outdoor receptacle support #84920
05/16/03 05:01 PM
05/16/03 05:01 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Don, good point, one that I missed. [Linked Image]

I would not want to see RNC used this way, and am glad it can be rejected.

Thanks, Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Outdoor receptacle support #84921
05/18/03 07:08 AM
05/18/03 07:08 AM
T
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
Here's the Arlington Industries Gard-N-Post that HotLine1 mentioned.
http://www.aifittings.com/whnew43.htm

Re: Outdoor receptacle support #84922
05/18/03 08:21 PM
05/18/03 08:21 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Iwire:
As I mentioned..."in most cases", I took that route as to not open the proverbial can of worms.
As resqcapt pointed out, PVC doesn't fly (same for EMT),it's rigid or intermediate, two conduit entry. etc.

And BTW, BOBWK....you said "two 2" PVC into the box..." something don't sound right there either????

John


John
Re: Outdoor receptacle support #84923
05/18/03 08:45 PM
05/18/03 08:45 PM
G
Gwz  Offline
Member
Joined: Apr 2002
Posts: 197
It appears to me that RNC shall not be used for the proposed installation.

See 352.10(H), 352.12(B), 352.12(C).


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,863 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.031s Queries: 14 (0.007s) Memory: 0.9931 MB (Peak: 1.1546 MB) Zlib enabled. Server Time: 2018-01-23 00:02:18 UTC