wires to panel box #84718
04/28/03 09:07 AM
04/28/03 09:07 AM
R
Reel-Break  Offline OP
Member
Joined: Apr 2002
Posts: 178
nc
Is there a violation with this:I installed a 200 a panel drilled a 2" hole in floor under panel installed nail plate ran all my circuit wiring through this hole.I also installed a 2" conduit on the bottom also I caped it off under home for future use.The home owner called said the inspector didn`t like all the wires coming through the hole and the abandon pipe installation.She said he left no code numbers of violation.Can you see a problem the way it was done code wize?Thanks in advance.

2017 / 2014 NEC & Related Books and Study Guides
Re: wires to panel box #84719
04/28/03 10:55 AM
04/28/03 10:55 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
It could be a bundling/derating issue per 310.15 (B)(2). And also, if you want to use the 2" conduit for future use, I don't believe it can be concealed. I can't remember the reference though.

Re: wires to panel box #84720
04/28/03 04:12 PM
04/28/03 04:12 PM
D
dana1028  Offline
Member
Joined: Jan 2002
Posts: 163
San Carlos, CA
"all my circuit wiring" - is it fair to assume NM cable? (aka: Romex) - if so -
336-6(b) requires, "where passing through a floor, the cable shall be enclosed in RMC, IMC, EMT, Sch. 80 PVC, listed surface metal or nonmetallic raceway or other metal pipe extending at least 6" above the floor."

Don't see any reference regarding
'concealed' or anything about the 'abandoned pipe installation.'

Re: wires to panel box #84721
04/28/03 05:16 PM
04/28/03 05:16 PM
N
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
Call the inspector and ask for a code reference. If he cannot or willnot provide one, talk to his boss. The inspectors are supposed to know what they are doing, and know the code.


ed
Re: wires to panel box #84722
04/28/03 06:32 PM
04/28/03 06:32 PM
S
spyder  Offline
Member
Joined: Oct 2002
Posts: 210
Massachusetts
Is this a flush mount or surface mount installation?

If its flush mount then I do not see a problem with your cable installation. The bundling argument is kinda weak for residential, as there are very few continuous loads in residential. If its a loose bundle it should be okay.

If its surface mount, then his problem maybe with no protection from physical damage.

Since he has a problem with your spare conduit, I would terminate it in a proper size pull box.

Re: wires to panel box #84723
04/28/03 09:42 PM
04/28/03 09:42 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
See 312.5 (C) 2002 NEC regarding the pipe.
As far as derating for bundling, I don't see that the code distinguishes between continuous or non-continuous load. If the cables are bundled in excess of 24", the inspector would have a valid point.

[This message has been edited by Redsy (edited 04-28-2003).]

Re: wires to panel box #84724
04/29/03 06:25 AM
04/29/03 06:25 AM
S
spyder  Offline
Member
Joined: Oct 2002
Posts: 210
Massachusetts
Redsy,

My point about continuous or non-continuous loads was heat. The reason we derate conductors is to avoid a heat problem. Most conductors in residential are never fully loaded, let alone continualy loaded. Since they are not fully loaded then aren't they already derated?

If you go by the literal wording of the code, then I agree you are correct.

Re: wires to panel box #84725
04/29/03 07:40 AM
04/29/03 07:40 AM
R
Reel-Break  Offline OP
Member
Joined: Apr 2002
Posts: 178
nc
Hey Redsy that was the issue he didn`t realize the conduit was capped at the other end under home.But he sited the wiring being bundled in excess of 24 in.Ok but they are actually spread out going to the romex connectors in the panel and under the house they aren`t really bundled they are somewhat close but you know what I mean I told him I`d spread out as far as possible so he`s comming back to see.I guess there`s a gray area here up to him if he thinks they are bundled still.This is a flush mount residental.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,583 Are you busy
180,379 Re: Forum
170,856 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 14 (0.004s) Memory: 0.9911 MB (Peak: 1.1488 MB) Zlib enabled. Server Time: 2018-01-21 20:28:31 UTC