#84387 - 03/25/03 09:57 PM Male plug on NM Cable  
TNMarch  Offline
Junior Member
Joined: Mar 2003
Posts: 3
Knoxville, TN USA
Can I use a male plug on romex (NM-B) cable......legally?
Thanks for your information.


If I knew it all....I wouldn't be here asking!!

2017 / 2014 NEC & Related Books and Study Guides

#84388 - 03/25/03 10:02 PM Re: Male plug on NM Cable  
SvenNYC  Offline
Member
Joined: Aug 2002
Posts: 1,691
New York City
No. I believe cord caps are only listed for flexible temporary cords.


#84389 - 03/25/03 10:07 PM Re: Male plug on NM Cable  
TNMarch  Offline
Junior Member
Joined: Mar 2003
Posts: 3
Knoxville, TN USA
Thankyou so much for your help on this. I'm by no means an electrician......but I've seen this dozens and dozens of times, even in my old job (OSHA), and I know I cited this, but I had a client give me a fit today, and I just couldn't remember how I had cited this!!!! Any NEC to go with this would be GREATLY appreciated.
First time posted on this board......This is one of the most impressive things I've ever seen on the internet!!!!
Again, thankyou sooo much
See ya'
Brian


If I knew it all....I wouldn't be here asking!!

#84390 - 03/25/03 10:15 PM Re: Male plug on NM Cable  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,311
This would be a rating/listing issue, however i would like to know if there is a male cord cap that is applicable to 527.4(C) ex. out there?


#84391 - 03/25/03 11:14 PM Re: Male plug on NM Cable  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
It’s likely that wire terminations in cord caps are intended/listed for solid conductors.


#84392 - 03/26/03 01:43 AM Re: Male plug on NM Cable  
SvenNYC  Offline
Member
Joined: Aug 2002
Posts: 1,691
New York City
Bjarney

I was in a lighting section of a department store last year here in New York's Chinatown and noticed that the receptacle bar (those Wiremold raceway things) that all the table lamps were plugged into was terminated in a length of AC ending with an armored heavy-duty cap (you know the ones with the grounded metal husk on them).

Needless to say it gave me the willies...especially if the end of the AC going into the plug didn't have a little "Red Devil" to protect the wires. Scrape...scrape....KA-POOF!!

Passing by some construction sites, I've seen Romex hooked up to cord caps, usually the square yellow plastic ones.

What makes me say "no" to this is common sense.

I mean...stop and think about it for a second:

The terminal screws inside a plug are small and there's not enough space to properly bend a stiff solid wire around them, so what you might have is a little stump of conductor clamped under a screw. I guess that could lead to overheating....

Also, since the insulation on AC or NM is so stiff, the cap's strain relief (if it has one) doesn't have anything to "bite" on. There's practically no "give" so the wire can also break inside the plug's housing, dance around eventually short something out in there.

Please note that these are not scientific observations, just common sense from what I've seen.

Disclaimer: I am NOT an electrician, so I tend to err on the side of caution. Also, the instruction sheets packed with some heavy-duty plugs and connectors I've used say it is to be used only with flexible cord - type X and wire gauge size Y.

[This message has been edited by SvenNYC (edited 03-26-2003).]


#84393 - 03/26/03 02:12 AM Re: Male plug on NM Cable  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
There was a recent photo posted at E-C.net picturing {3?} NM cables with cord caps—that may have been found above a suspended ceiling, ostensibly powering lay-in fluorescent fixtures.


#84394 - 03/26/03 03:00 PM Re: Male plug on NM Cable  
dana1028  Offline
Member
Joined: Jan 2002
Posts: 163
San Carlos, CA
UL gives little information about conductors for 'attachment plugs' - category AXGV in their Green Book - however, as there are so many different types of plugs it seems to indicate the mfr. would give specific information about the types of conductors/cords acceptable for use with a particular plug.


#84395 - 03/26/03 03:38 PM Re: Male plug on NM Cable  
GEO  Offline
Member
Joined: Mar 2003
Posts: 47
Lancaster,Pa
STILL LOOKING-- but for now you purchase a cord cap not romex cap GEO
must be approved for the use
ul white book states FLEXIBLE cords or cable
romex protected, supported,
etc.etc etc---- WILL NOT ACCEPT and it looks ulgy too

[This message has been edited by GEO (edited 03-26-2003).]


#84396 - 03/26/03 09:52 PM Re: Male plug on NM Cable  
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
See if any of this helps: http://www.osha.gov/pls/oshaweb/owadisp.show_document?p_table=STANDARDS&p_id=10706#1926.405(g)

Also: http://www.osha.gov/SLTC/etools/construction/electrical_incidents/cords.html
http://www.osha.gov/SLTC/etools/construction/electrical_incidents/flexiblecords.html


Page 1 of 2 1 2

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 15 (0.002s) Memory: 0.8172 MB (Peak: 0.9917 MB) Zlib enabled. Server Time: 2017-07-24 06:42:51 UTC