#82576 - 11/28/02 04:54 PM Table 310.15(B)(2)(a)  
Bobby Mercier  Offline
Junior Member
Joined: Nov 2002
Posts: 7
St-Georges,Quebec,Canada
If i use 3c10awg MC cable for cabling 10 hp 460V motors, in accordance with table 310.15(B)(2)(a), i can make a bunch of 10 of this cable. My question is how many space it should have bettween this bunch of cables and another bunch of cables. (i mean in a ladder cable tray)

[This message has been edited by Bobby Mercier (edited 11-28-2002).]


2017 / 2014 NEC & Related Books and Study Guides

#82577 - 11/29/02 09:17 AM Re: Table 310.15(B)(2)(a)  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Space means just that, as in no contact between the bundles. Since no specific dimension is given, if you can see a crack of light between the bundles, they meet the definition of the word "spaced."


Few things are harder to put up with than the annoyance of a good example.

#82578 - 11/29/02 09:24 AM Re: Table 310.15(B)(2)(a)  
Bobby Mercier  Offline
Junior Member
Joined: Nov 2002
Posts: 7
St-Georges,Quebec,Canada
Thanks for our reply TOM


#82579 - 11/29/02 01:38 PM Re: Table 310.15(B)(2)(a)  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Look at 392.11(A). This section is not real clear to me, and (A)(1) appears to conflict with (A)(3).
Don


Don(resqcapt19)

#82580 - 11/29/02 03:20 PM Re: Table 310.15(B)(2)(a)  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Don has a very good point & I could see a fistfight or two breaking out over it. Maybe you need to space the bundles 1 bundle diameter apart.

I feel I correctly answered your question about space in the ordinary sense, but I didn't do so in the context of your question.

In any case, since you are dealing with #10 conductors, it appears that 310.15(B)(2)(a) would require a derating to 45%. Therefore, #10 would be OK since its final ampacity is more than 125% of the 14 amps the motor draws.

It would be interesting to apply Exception 5 to 310.15(B)(2)(a) by using #12 & supporting on bridle rings instead of cable tray. What do you think?


Few things are harder to put up with than the annoyance of a good example.

#82581 - 11/29/02 10:58 PM Re: Table 310.15(B)(2)(a)  
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
Don
I believe that 392.11(A)(1) applies to the cable assembly. eg a 10-3 mc cable vs a 10-5 mc cable where you may have more than 3 current carring conductors in that one cable.
I believe that 392.11(A)(3) applies to the total # of cable assemblies installed in the tray.
Keeping cable assemblies seperated is a good practice.


ed

#82582 - 12/06/02 09:49 AM Re: Table 310.15(B)(2)(a)  
Bobby Mercier  Offline
Junior Member
Joined: Nov 2002
Posts: 7
St-Georges,Quebec,Canada
I think if i respect table 392.9 i don't have to derate cable.

Do you thing it's OK



Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,809
Joined: April 2002
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.002s) Memory: 0.7839 MB (Peak: 0.9375 MB) Zlib enabled. Server Time: 2017-04-28 10:20:27 UTC